Step 2. Enter Point Limits

The Limits tab is available in the Point Properties (and Data Item ) dialog box:

For device or virtual analog points:

When the General tab is in Advanced view.

  • Range limits configuration.
  • Setpoint limits configuration.

Range Limits configuration

Values below a low range limit and above a high range limit will display as an unavailable point value.

Range limits:

  • Apply to only the first element of an array point.
  • Can be very useful if you want to exclude meaningless data from CIMPLICITY functions.

Enter the low and high limits in the Range limits box for the converted value of the point.

Example

  • A PLC gives raw data in counts from 0 to 1000.
  • The raw data represents temperatures between -500 °C and 500 °C.
  • Values above 200 °C or below -200 °C are considered to be out of range.
  • The point's value displays as follows.
Point value Value that displays
Below -200 °C Unavailable
Above 200°C Unavailable
Between -200 °C and +200 °C Current
guide: Guidelines for Unavailable Range Values during Runtime

When the project is running, values exceeding the range limits are handled as follows:

If the range limit is exceeded:
During runtime
  • The point value on CimView screens displays the default text until the point comes back within raw limits.
  • Point Control Panel displays asterisks (******) for the point value until the point comes back within raw limits.
At startup
  • The point value on CimView screens displays the default text until the point comes back within raw limits.
  • Point Control Panel displays asterisks (******) for the point value until the point comes back within raw limits.
If the RAW_LIMIT_ALARM global parameter is set to:
YES An alarm is generated when a point's value first exceeds its range limits. When the point value returns to within its range limits, the Alarm State will be set to Normal.
NO No alarm will be generated.

Setpoint limits configuration

Setpoint entries during runtime must be within the limits entered in the Setpoint limits box.

If a user enters a value below the low setpoint limit or above the high setpoint limit, the value will not be accepted.

Enter the Low and High limits in the Setpoint limits box.