Step 3. Configure Scan Time
The Status Log file is periodically scanned to check for records that have been added to it since the last scan. You can specify the periodic rate at which the Status Log file is scanned for added records value, using the global parameter COR_LOG_RP_SCAN_TIME or from the Advanced tab of COR_LOG Table Properties.
About this task
Procedure
- From Global Parameters: In the CIMPLICITY Workbench window, in the left pane, expand Project, expand Advanced, and then select Project Parameters.
-
In the list of parameters, double-click
COR_LOG_RP_SCAN_TIME, enter a value, and then select
OK.
Note: The default value of COR_LOG_RP_SCAN_TIME is 300 seconds. The minimum value allowed is 15 seconds and the maximum value allowed is 3600 seconds.
From COR_LOG Table Properties
About this task
Procedure
- In CIMPLICITY Workbench, double-click Database Logger.
- Right-click COR_LOG, and then select Properties.
- Select the Advanced tab.
-
In Scan rate field, enter the value at which you want to
scan the Status Log for the records.
Note: The default value of COR_LOG_RP_SCAN_TIME is 300 seconds. The minimum value allowed is 15 seconds and the maximum value allowed is 3600 seconds.
- Select OK.