AlarmUpdateEx (statement)
Syntax | AlarmUpdateEx Project$, AlarmId$ , ResourceId$ , Action%, DateTime, IsUTC [ , AlarmMessage$ [ , UserId$ [ , RefId$]]] | ||||
Parameter | Description | ||||
Project$ | String. The project to update the alarm on. An empty string "" indicates the current project. | ||||
AlarmId$ |
String. The ID of a non-point or point Alarm that is listed in the right-pane of the Workbench>Alarms section.
Note:
Non-point alarms must be a $CIMBASIC alarm type for all details, including the alarm message, to display correctly in an Alarm Viewer.
Point alarms are not $CIMBASIC alarms. As a result, there are limitations and guidelines to be aware of if those alarm IDs are used in the script.
|
||||
ResourceId$ | String. The Resource ID to update the alarm against. Used to control routing of the alarm. | ||||
Action |
Integer. Indicates whether to acknowledge or reset the alarm. Use the following constants to perform an acknowledgment and a reset.
|
||||
DateTime | The DateTime parameter depends on the script type. | ||||
CimBasic |
Date Variant
The Date and Now functions return the Date Variant type.
|
||||
.NET C# | System.DateTime type | ||||
VB .NET | System.DateTime type | ||||
IsUTC | BOOLEAN Whether or not the passed in timestamp is UTC. | ||||
TRUE | The DateTime parameter is a UTC timestamp | ||||
FALSE | The DateTime parameter is not a UTC timestamp | ||||
Note: If you do not use UTC time, you will be responsible for making sure your system’s Time Zone settings, including DST, are properly set.
|
|||||
Message$ | String. The update alarm message to display. Note: This string is substituted into the first variable field of the Alarm's message. | ||||
UserId$ | String (optional). The User ID that updated the alarm. | ||||
RefId$ | String (optional). A Reference ID used to distinguish identical alarms. | ||||
Master | BOOLEAN (optional). By default on a computer with Server Redundancy, alarms sent by the standby computer's Event Manager are ignored. To allow an alarm to be generated from a script on a standby computer, set Master to True. | ||||
CimBasic Example |
|
||||
.NET C# Example |
|
||||
VB .NET Example |
|
Guidelines: AlarmGenerateEx and AlarmUpdateEx
- Message$ limitations and guidelines.
- Non-Point alarm requirements.
- Point alarm guidelines.
Note: Guidelines also apply to
AlarmGenerate
and
AlarmUpdate
.
Message$ Limitations and Guidelines
Messages that display in the Alarm Viewer draw from the following sources and have the following limitations.
The message, which is a string, is substituted into the first variable field of the alarm's configured message.
Message: User-defined alarm
The substituted string will be the first %s in the Alarm Definition dialog box>Alarm Message field.
|
|||
Message
: Point alarm ID
The substituted string will be the first variable field (%VAL , %ID ) in an Alarm Definition dialog box (or Point Properties dialog box)>Alarm Message field.
However, if a point alarm ID is used in an
AlarmGenerateEx
or AlarmUpdateEx script, because the alarm is not a $CIMBASIC alarm, the message will most likely not display as you would expect.
Examples
The entry in the Alarm Message field includes text and more than one variable
POINT01 is %VAL : %STATE
If the code:
|
|||
Does not include a message |
POINT01 is :BAD FIELD
|
||
Does include a message "Point in alarm state." |
POINT01 is Point in alarm state. BAD FIELD
|
Non-Point Alarm Requirements
The alarm definition (in an Alarm Definition dialog box) for a non-point alarm must include the following values.
Alarm type |
$CIMBASIC alarm.
|
Alarm message |
%s
|
Point Alarm Guidelines
When an alarm is generated using a point alarm ID, the alarm that is generated is actually no longer a point alarm.
However, like its point alarm counterpart, it also is not a $CIMBASIC
alarm.
- The alarm message may not display correctly.
- A unique alarm in CIMPLICITY is defined by the Alarm ID, Resource ID and Reference ID combination.
Each unique alarm can be displayed as a distinct entry in the Alarm Viewer.
If the actual point alarm is in alarm state and displays in the Alarm Viewer, using the same alarm ID in:
-
AlarmGenerateEx
will generate a separate alarm from the point alarm. -
AlarmUpdateEx
will acknowledge and/or reset the actual alarm depending on the command(s).
Note: If only the generated alarm is listed AlarmUpdateEx
will acknowledge and/or reset that alarm.
- Non-unique alarms are stacked, so that the user only sees the most recent occurrence. In general, the Resource ID is used to control the routing of alarms to users.
- The Reference ID is used by an application to distinguish between different instances of the same alarm.